How to bring INET SCU1200/1280 controllers online after transitioning to Security Expert

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to bring INET SCU1200/1280 controllers online after transitioning to Security Expert
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • RichardWa
    RichardWa

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1288 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to bring INET SCU1200/1280 controllers online after transitioning to Security Expert

Ensign RichardWa Ensign
‎2021-05-17 05:51 AM

on ‎2021-05-17 05:51 AM


Issue

After transitioning an INET security system to Security Expert, SCU1200 and SCU1280 controllers do not come online

Product Line

Security Expert, TAC INET

Environment

  • Security Expert Controller (SP-C)
  • I/NET SCU1200
  • I/NET SCU1280

Cause

The INET-to-Security Expert transition brings each SCU1200/1280 into Security Expert as an Input Expander but there is a known issue that causes the devices to remain offline. R&D is working on a fix.

Resolution

The workaround for bringing a SCU1200/1280 controller online in Security Expert is to create a Reader Expander and then edit the inputs and outputs associated with the SCU1200/1280 to point to the Reader Expander you’ve just created.

 

Important: 

Create a backup of your Security Expert database before proceeding with the instructions that follow.

 

For a transitioned SCU1200/1280, create a Reader Expander as follows:

  1. In Security Expert, navigate to Expanders > Reader Expanders.
  2. Choose a Controller from the drop-down list.
  3. Click the Add icon.
  4. Define a Name for the expander. 
    The transition tool would create a name like SCU1200 <703503> for the expander.  In this example, the SCU’s link address is 70, its station address is 35, and its point address is 3. When manually defining the name of the new expander, you may wish to use this naming convention to keep the system uniform.
  5. Set the Physical Address of the expander. 
    This address should be 1 higher than the point address of the SCU.  So, for SCU1200 <703503>, the point address is 3 (703503) and so the physical address of the expander should be set to 4.
  6. Set Port 1 Network Type to “Third Party Generic”.
  7. Set Port 2 Network Type to “Third Party Generic”.
  8. Expand the Commands section and enter the following commands:
          PortOne=INET
          HardwareType=INET
  9. Navigate to the Reader 1/2 tabs and perform the following steps:
    1. Set Reader 1/2 Keypad Type to “None”.
    2. Uncheck Allow Reading Opened/unlocked.
    3. Uncheck Display Card Detail when Invalid.
  10. Navigate to the Reader 1/2 Options tabs and perform the following steps:
    1. Uncheck Door Sense Enabled.
    2. Uncheck REX Enabled.
    3. Uncheck Invert REX Input R1/2.
    4. Uncheck Always Allow REX R1/2.
  11. Save the expander.
  12. When presented with the Configure Module wizard, perform the following steps:
    1. Set Inputs to 0.
    2. Set Outputs to 0.
    3. Uncheck Add Trouble Inputs.
    4. Uncheck Add Doors.
    5. Click Add Now.

 

Edit the inputs associated with a transitioned SCU1200/1280 as follows:

  1. In Security Expert, navigate to Programming > Inputs.
  2. For each input associated with the SCU1200/1280, change the Module Type to “Reader (RD)”.
  3. Save the input.

 

Edit the outputs associated with a transitioned SCU1200/1280 as follows:

  1. In Security Expert, navigate to Programming > Outputs.
  2. For each output associated with the SCU1200/1280, change the Module Type to “Reader (RD)”.
  3. Save the output.

 

When you have finished with all of the steps above, perform a Module Update on the Reader Expander.  Repeat these steps as necessary for other SCU1200/1280 devices.  Once you have verified all SCU1200s/1280s are working properly, you can delete the Input Expanders that were created by the transition tool since they are now unnecessary.

Labels (2)
Labels:
  • EcoStruxure Security Expert
  • TAC INET
Tags (8)
  • Find more articles tagged with:
  • 1200
  • 1280
  • offline
  • online
  • RichardWatson21
  • scu
  • SCU1200
  • SCU1280
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.