How to avoid EBO license damage in virtual environment

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to avoid EBO license damage in virtual environment
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Mahmoud_Sayed
    Mahmoud_Sayed

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
10471 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to avoid EBO license damage in virtual environment

Kirk Mahmoud_Sayed Kirk
‎2023-07-31 05:49 AM

Issue

The EBO license is activated on a virtual machine, need to make sure that it will not get damaged.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation Enterprise Central
  • Building Operation Workstation

Cause

Scenarios leading to broken Trusted Storage (license damage), when license is activated on a Virtual Machine. In some cases, the License Administrator can be used to repair the license, and in other cases, product supported will need to be contacted.

Resolution

FlexNet documentation explains how licensing in virtual machines works, what causes license damage, and how to avoid license damage. Make sure that documentation is related to the FNP version (FlexNet publisher) used by installed EBO, ex. EBO V4.0.2 uses version 2021 (11.18.1) and EBO V5.0.2 uses FNP V2022 R3 (11.19.2). 

You can also check the FNP version by checking the properties, details of lmadmin.exe file located in C:\Program Files (x86)\Schneider Electric EcoStruxure\Building Operation x.x\License Server

lmadmin version.png

Binding elements for licenses activated on a virtual machine:

  • FlexNet publisher documentation lists three binding elements for virtual machines, all of which are deal breakers: MAC address, UUID, and Generation ID, refer to Binding in a Virtual Environment (revenera.com) 

Scenarios that can cause license damage (Trusted-Storage Breakage):

  • In the attached FlexNet White Paper: Understanding Virtualization Features in FlexNet Publisher, Page 9, details binding variables and which scenarios can change each binding element.
  • Page 11 in the same white paper, Recovering from a Binding Break in TS, explains common scenarios leading to broken TS and if a license can be repaired. 
  • WebHelp article EcoStruxure Building Operation Software License Repair, explains other reasons for license damage, for physical or virtual machine. 
  • Please contact your local support if the License Administrator can't repair the license.

Best Practices to avoid Trusted-Storage Breakage:

  • To minimize license damage, follow the below steps before making changes to the bindings elements or moving EBO to a new VM.
    1. Make a backup of EBO, Backing Up EcoStruxure BMS Servers Manually
    2. Return all licenses, Returning an EcoStruxure Building Operation Software License.
    3. Verify that all licenses have been returned for all used Entitlements by logging in to https://licensing.se.com.
    4. Perform your operation.
    5. Activate the licenses again, Activating EcoStruxure Building Operation Software Licenses.
  • FlexNet lists best practices that can also be followed to avoid trusted storage breakage: Best Practices (revenera.com)
Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
Tags (4)
  • Find more articles tagged with:
  • MahmoudSayed23
  • MahmoudSayed24
  • MahmoudSayed25
  • RobertAndriolo24
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore