Issue
Selecting the appropriate IO system on a Continuum Net Controller (NC1 or NC2)
Product Line
Andover Continuum
Environment
- CX9900
- CX9940
- CX9680
Cause
Controller configuration
Resolution
Continuum Net Controllers can support three different IO systems, ACC-LON, LonMark XDriver and the legacy LBus. Only one IO system can be selected, the controller must be re-started after the selection is made.
The document Selecting IO system in Continuum NetController has instructions on selecting the desired IO system for the controller.