How to Change the Point Address of an Object in I/NET Graphic?
  • How to Change the Point Address of an Object in I/NET Graphic?
  • sesa145087_brid
    sesa145087_brid
‎2018-09-11 06:28 AM
As long as an object is inserted in I/NET graphic, it seems that the referred address can't be changed.
I/NET
The address reference of the object in I/NET graphic needs to be changed.
In the current newest version of I/NET, there is a function called Address Conversion Utility. When editing a graphic:
  1. Click File > Address Conversion
  2. Choose the points that you want to change addresses on
  3. Click on the address you want to change and change it
  4. Click OK
The address reference in I/NET graphic object has been changed. You can change all the Link, Station, Point and Bit addresses of these points.