How to Calculate the M&B for a Slide on a Slide Stat
  • How to Calculate the M&B for a Slide on a Slide Stat
  • Tom_Poovey
    Tom_Poovey
‎2018-09-06 03:30 PM
Determine the correct conversion coefficients for a Slide Stat
I/NET Software
Station Parameters
Programming a Slide Stat to read the correct input values.
  1. Go to the Controller > Station Parameters > Conversion Coefficient Option.
  2. Add the M of 1 and a B of 0. Doing this will give the "Count" of the parameter.
  3. Once you determine the counts at both end of the slide position. Then calculate the actual M & B for the side.
  4. Once the "Counts" in Step 2 are determined, place these values in the "Counts Low" and "Counts High" slots.
    In this example, a 5 degree range from the low slide to the high slide is desired. Use -2.5 for the "Units low" and +2.5 for the "Units high" setting. Then select the OK button to give the actual M&B for the Slide coefficient.
  • TAC INET
  • 7622