How often does a Bacnet MSTP B3 controller broadcast alarms?
  • How often does a Bacnet MSTP B3 controller broadcast alarms?
  • Carl_Slack
    Carl_Slack
‎2018-09-06 02:13 PM
How often is the Bacnet MSTP B3 polled for alarms?
Bacnet MSTP
Andover Continuum B3 MSTP controller
Determining the process of MSTP B3 alarming
The Bacnet B3 communicates on a token passing Bacnet MSTP protocol. When a B3 is configured for alarming and an alarm occurs, it will broadcast the alarm when the controller has the token.
Labels (2)