How much ethernet bandwidth do LonWorks systems consume using Loytec L-IPs, iLons, etc.?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How much ethernet bandwidth do LonWorks systems consume using Loytec L-IPs, iLons, etc.?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • chris_clerc
    chris_clerc
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1847 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How much ethernet bandwidth do LonWorks systems consume using Loytec L-IPs, iLons, etc.?

Picard Product_Support
‎2018-09-06 03:12 PM

Issue

How much ethernet bandwidth do lonworks systems consume using Loytec L-IPs, iLons, etc.?

Environment

  • TCP/IP ethernet network

  • LNS System

Cause

IT professionals will sometimes hesitate to allow the control system to use the same TCP/IP network as the internet, phones, etc. They may ask what the expected bandwidth usage will be before granting access.

Resolution

It is impossible to explicitly state how much bandwidth a LonWorks system will consume on the ethernet. It depends heavily on the amount of LON traffic being sent by the controllers. The routers themselves do not produce traffic, they only pass the traffic onto and off of the ethernet. The traffic is created by the LON devices, Xenta controllers, Vista and LonMaker or other HMIs.

Vista can create a maximum of 15 LON telegrams/second. This is very little traffic with respect to IP bandwidth. Unless you have made bindings into the LNS NI (which we never do in a Vista-scenario, since Vista cannot read these) there is basically nothing at all going out from LonMaker/LNS unless you are commissioning devices. Starting the LonMaker Browser also generates traffic. But this is also normally just in the design phase of the network, not in "operating mode".

SNVT bindings or TAC network variables from one LON network to another over the IP channel also generate traffic. A typical Xenta can produce 2 SNVTs propagation/second and/or maybe 10 TACNV. This is not much (as IP-traffic), but if there are hundreds of nodes communicating simultaneously all passing through L-IP gateways, the amount of IP traffic will grow.

If you are using a Loytec L-IP, it uses a protocol feature called "packet bunching". Before it sends out a packet on the IP side, it waits for an adjustable time (Aggregation Time, default = 16ms) if some packets are following, which have to be sent to the same IP addresses. If some packets are following, it puts the packets in the same IP frame and sends it all together in a single IP packet. The receiving node unpacks it and makes multiple EIA-709 (Lonworks) packets again.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 1737
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore