How many stages of heating can be used with a Xenta 102-AX?
  • How many stages of heating can be used with a Xenta 102-AX?
  • Anonymous user
‎2018-09-06 03:08 PM
Last Updated: Administrator DavidFisher Administrator ‎2019-05-24 09:43 AM
TAC Vista
Xenta 102-AX
A Xenta 102-AX can be configured in the plug-in for up to three stages of heat, but there are only two heating outputs.
The 102-AX can be used with up to 3 stages of heat.
  1. First stage is one strip
  2. Second stage turns off the first strip and energizes the second strip
  3. Third stage turns on both strips.
This can be utilized very nicely for boxes where, for example, the first stage is 3kW and the second is 6kW. The third stage would provide 9kW.
Refer to the 102-AX Software and Hardware Reference Guide Chapter 2 page 21.