Issue
How many Modbus TCP Clients can be connected to Vista via an Xenta 913?
Product Information
TAC Vista
Environment
- Vista 5.1.X
- Xenta 913 5.1.X or later
- Xenta 511 5.1.5 or later
- Xenta 701 5.1.5 or later
- Xenta 711 5.1.5 or later
- Xenta 721 5.1.5 or later
- Xenta 731 5.1.5 or later
Cause
When planning a system it's important to know how many devices are required.
Resolution
A maximum of 40 Modbus TCP clients are supported when communicating via a Xenta 913, Xenta 511 or Xenta 700. Each TCP Client may have up to 100 Modbus devices (see page 4 in the datasheet).