Issue
How does the controller-resident schedule work in a Revision 11.x MicroSmart controller?
Environment
MicroSmart controllers revision 11.x and 10.x
Cause
Main DMS panel and/or NC panel were removed.
Resolution
With the loss of schedule control from the DMS or NC, each controller has two built-in schedules numbered 1 and 2.
The Start/Stop point requiring a schedule can be assigned either one of these schedules followed by a letter A or letter B.
Letter A stands for 'always' and letter B for 'backup'.
With no DMS or NC present, enter the schedule as 1/A or 2/A. Assign 'off' and 'on' times as required.
Remove any reference to a DMS or NC schedule number (i.e. set it to a value of 00).