How does the IO Module communications bus operate?
  • How does the IO Module communications bus operate?
  • sesa139513
    sesa139513
  • PaulFr
    PaulFr
‎2018-09-06 10:03 AM
How fast are the IO Modules polled by the Netcontroller?
NCII, Netcontroller CX9900
IO Modules
UI-8-10, DI-8, DI-6-AC, MI-6, DM-20, AO-4-8, DO-4-R, DO-6-TR.
Information on the update speed of the I/O Modules is required.
It is a polling network with the NCII as the master polling the slave IO Modules:
  • Utilizes a polling protocol in which information is retrieved from I/O modules
  • NetController polls each I/O module by Module ID number
  • Modules are polled at a 50ms rate
  • If Less than 4 modules, the polling rate is 200ms
  • 14423