How do you configure a meter reading that is greater than 10,000.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How do you configure a meter reading that is greater than 10,000.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • Gary
    Gary

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1237 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How do you configure a meter reading that is greater than 10,000.

Picard Product_Support
‎2018-09-07 11:52 PM

Issue

MicroNet controller objects have a maximum allowable value of 10.000

Environment

 

MicroNet

Meters

VisiSat

Xbuilder

Vista 5

Cause

MicroNet controller objects have a maximum allowable value of 10.000 some meter readings require a greater value.

Resolution

1. In VisiSat add two counter objects.

Link the Rollover pulse output of the first counter to the Count input of the second Counter object.

Fig 1.

Counter Object 1 is used for the 0 - 999 part of the meter count.

Counter Object 2 is used for the 1000 - 1,000,000 part of the meter count.

2. In the Xenta 731 add a Menta object and program shown below in fig 2 is one example.

Fig 2.

This Menta code multiplies counter object instance 2 by one thousand and adds the sum with counter object instance 1 giving an output for total meter reading of up to 9,999,999.

3. This then can be added to value, graphic ETC pages.

 

 4.  If you would like to download an example click on your preferred option below.

Click here for the VisiSat project.

Click here for the Xbuilder project. 

Click here for the Vista database.

Click here for All three.

Labels (2)
Labels:
  • Satchwell MicroNet
  • TAC Vista
Attachments
Meters VisiSat.zip
Meters Xbuilder.zip
Meters Vista.zip
Meters VisiSat - Xbuilder- Vista.zip
Tags (1)
  • Find more articles tagged with:
  • 5134
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore