Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

How do I tune the response of a reheat temperature control loop?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How do I tune the response of a reheat temperature control loop?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1297 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How do I tune the response of a reheat temperature control loop?

Picard Product_Support
‎2018-09-06 12:24 PM

Issue

Have used tuning parameters that have worked good other places but at this site the loop output hunts continuously.  How do I properly tune this PI loop?

Environment

MNL-V2 or other temperature controller

Proportional hot water valve for the reheat control.

Cause

 Loop was tuned too tight causing continuous hunting that resulted in premature failure of the actuator.

Resolution

The following information is paraphrased from a number of previously published HVAC controls documents.

  1. Using only proportional control, adjust the Throttling range (TR) until the loop control is stable with no oscillation. The desired control range x 2.5 is a good TR to start with.  When the loop is still oscillating, note the period of oscillation (in minutes). You may need to increase the TR to 25 or more to achieve stability in the loop output.  You must achieve stable control before continuing.  If proportional control cannot stabilize the loop, adding integral and/or derivative will cause further instability.
  2. Make a step change (5 to 10%) in the setpoint.  If the system does not stabilize after a few minutes, repeat step 1.
  3. Increase the TR by an additional 5% to 30%.
  4. Use the following formula to calculate the initial value to be used for the integral value:
          i = 1 / [ ( Loop period in Minutes ) x 2 ]
  5. Monitor loop to evaluate response,  If the response is slow with integral action, increase the "i" value slightly.  It may be necessary to upset the loop, by changing the setpoint, to get a good test of the loop response.  The final integral value is typically in the range of 0.05 to 0.5.
  6. In most cases HVAC control loops do not require derivative action.  Improperly tuning the derivative action can result in poorer control than without any derivative action.  The following formula can be used to determine a starting value for the derivative value:
         d = (Loop period in Minutes) / 8
    This value may need adjustment to optimize the control.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 7816
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of