Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

How do I rename I/A Series (Niagara) station name?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How do I rename I/A Series (Niagara) station name?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2350 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How do I rename I/A Series (Niagara) station name?

Picard Product_Support
‎2018-09-06 01:09 PM

Issue

Station was named incorrectly when first created.  Just copying the station folder or renaming the folder has no effect on the name of the station.

Environment

I/A Series R2 system (any version)

Cause

Station was named incorrectly when first created.  Did not realize name for the station did not match the desired naming convention used for the other stations in this facility.

Resolution

To rename a UNC station:

  1. Save the existing station database using the Admin Tool DbAdmin function.
  2. Use the Admin Tool DbAdmin function to get the station config.sys file and to convert it to an xml file (config.xml).  You will then have a config.sns and config.xml file in the existing station folder.
  3. Create the new named station folder under the stations folder under the current Niagara... installation folder.
  4. Copy the config.xml file from the existing station folder to the new station folder.  Copy any other folders that are under the existing station folder (graphics, etc) into the new station folder.
  5. Open the config.xml file (in the new station folder) with a TEXT or XML editor that can handle large files.  Two text editors that are know to work properly with large xml formatted text files are Notepad++ or EditPad.  These editors are both available for free via Internet.
  6. The existing station name typically first appears on lines 18 & 19 of the file.  Use the editor's Search and Replace function to globally change the existing station name to the new desired name.  Make sure that the there are no spaces or special characters in the new station name.  When specifying the existing station name, do not include the double-quote marks.
  7. Using the Admin Tool DbAdmin command, convert the edited config.xml file to config.sns.
  8. Use the Admin Tool "Install Station" function to load the edited station into the UNC.
     
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 6444
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore