How do I change a CX-9200 or a CX-99xx to a CX-9680 (Netcontroller II)
  • How do I change a CX-9200 or a CX-99xx to a CX-9680 (Netcontroller II)
  • sesa119747
    sesa119747
  • sesa101527
    sesa101527
‎2018-09-06 02:43 PM
  • Cyberstation
  • CX-9200
  • CX-99xx
  • CX-9680
Controller has changed and need to change the controller model number in Cyberstation.
If you are Using Cyberstation V1.74 with SP2, or Cyberstation V1.81 or greater, all you need to do to accomplish this change is to edit the existing controller (CX9200 or CX99xx). In the controller Type dropdown menu, select 9680 and OK the change. When you save the change you will be prompted with a warning that this change is not reversible. Once you OK that, the database will change all the appropriate system objects to be compatible with the Netcontroller II including system variables. The replacement CX9680 can then be reloaded from the Cyberstation and the conversion is complete.