Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

How do I calculate the pulse constant for an MNL-800 BI object configured for pulse input?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How do I calculate the pulse constant for an MNL-800 BI object configured for pulse input?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • WaynePeters
    WaynePeters
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1288 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How do I calculate the pulse constant for an MNL-800 BI object configured for pulse input?

Picard Product_Support
‎2018-09-06 01:40 PM

Issue

How do I calculate the pulse constant for an MNL-800 BI object configured for pulse input?

The Pulse Constant is a user entered pulse scaling value used by the pulse algorithm for calculating the output based on a pulses per second frequency. The range of the Pulse Constant value is 0.1 to 1000.

Environment

MNL-800

Cause

How do I calculate the pulse constant for an MNL-800 BI object configured for pulse input?

Resolution

Calculating the pulse constant requires the value to first be scaled to the equivalent pulse rate in seconds. Two examples are shown below.

The first example represents a water meter that provides a pulse that represents cubic feet per minutes. The meter generates one pulse per minute that represents a rate of 10 cubic feet per minute. The pulse constant calculates on a per second basis so the first step is to determine what one pulse represents as a rate per second.

1 pulse per minute / 60 seconds = 0.0166666 rate per second

Next, divide this value into the desired output when this pulse rate occurs. In this case, the rate value is 10 so the pulse constant is equal to 10 / 0.01666666 or 600.

The second example represents an electric meter that provides a pulse that represents KW. The meter generates one pulse every 0.5 second that represents a rate of 15 KW. The meter will pulse twice every second (1 second / 0.5 second). The pulse constant is calculated by multiplying the rate value by 2 or a pulse constant of 30. A meter pulsing twice per second will generate an output of 30 KW.

Reference the WorkPlace Tech Tool Engineering Guide - Binary Input object (F-26580) for more details.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 5469
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore