How can it be determined what LonWorks Program IDs are supported by the Niagara G3 system?
  • How can it be determined what LonWorks Program IDs are supported by the Niagara G3 system?
  • sesa116873_brid
    sesa116873_brid
‎2018-09-06 01:37 PM
G3 WorkBench (all builds)
N/A
  1. Create and install a test station on the localhost.
  2. Open the test station in WorkBench then add LonNetwork to Drivers from the lonworks Palette.
  3. Double-click on the LonNetwork.
  4. Double-click on the Local Lon Device listed under Database and set the following properties
    • Channel ID: 1
    • Subnet: 1
    • Node: 127 and click OK to accept changes.
  5. Right-click on LonNetwork and open the Lon Utilities Manager.
  6. Select the Local Lon Device then choose the Command of Reports and Sub-command of program Ids.
  7. Execute the command and a listing of all programIDs for the shadow objects found in the local My Module  library will appear.
  8. To save - highlight all program Ids and use “Ctrl C” to save to file.
  • TAC IA Series
  • 5545