Issue
How can it be determined if a new Niagara G3 ENC or new Niagara R2 UNC has the new boot flash?
Environment
- Niagara G3 ENC
- Niagara R2 UNC
Cause
Determine boot flash version.
Resolution
The best way to determine if the controller has the new or old boot flash is to compare the serial number on the printed circuit board with the numbers listed below:
UNC New Boot Flash (requires 529)
- UNC-410:Serial number 36218 or greater, shipped 6/16/10
- UNC-520:Serial number 36184 or greater, shipped 6/16/10
ENC New Boot Flash
- ENC-410:Serial number 263187 or greater, shipped 5/18/10
- ENC-520:Serial number 263122 or greater, shipped 5/13/10
If the serial number was removed or is not legible, contact Product Support Services for assistance. There is additional information available that will assist in determining the new and old boot flash.