Issue
How can a setpoint programmed using a nci-type snvt, in a MNL controller, be controlled and displayed in a Niagara R2 station?
Environment
MNL controllers
Niagara R2
Cause
Site programming was done years ago and the end customer wants to now add the ability to change a setpoint in all the MNL controllers from a Niagara R2 graphic. The setpoints were configured using a nci-type snvt (ex: nciSatConfig1).
Resolution
A nci-type snvt can be displayed and commanded from a Niagara R2 station. One method to provide both:
-
In the DynamicCmd object > Config tab, set it up like this:
-
Visual tab, set it up like this:
-
In the UnitConversion > Config tab, set it up like this: