How can a remote BACnet/IP network be accessed using the WorkPlace Commissioning Tool (WPCT)?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How can a remote BACnet/IP network be accessed using the WorkPlace Commissioning Tool (WPCT)?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa119747
    sesa119747
  • sesa116871
    sesa116871
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1553 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How can a remote BACnet/IP network be accessed using the WorkPlace Commissioning Tool (WPCT)?

Picard Product_Support
‎2018-09-06 02:43 PM

Issue

How can a remote BACnet/IP network be accessed using the WorkPlace Commissioning Tool (WPCT)?

Environment

  • BACnet/IP network
  • WorkPlace Commissioning Tool (WPCT)

Cause

Remote connectivity is needed to access a BACnet device that exists on an outside network where WPCT resides.

Resolution

When WPCT starts, it sends out a "whoIs" (broadcast) message. The responding devices send the reply ("iAm") using its IP address. If the responding device is on a private IP network that is using NAT or Port Forwarding to access the Internet, it is this private IP address that is populated in the "iAm" response. After the response, WPCT starts using directed messages using the address it received from the responding device. Private IP addresses cannot be routed through the public Internet. Therefore, NAT or Port Forwarding cannot be used to access remote BACnet/IP networks using WPCT.

There are two ways around this issue:

  1. Use a public IP address in the internal BACnet network
  2. Use a VPN to access the network

For more details, consult the I/A Series Micronet BACnet Wiring, Networking, and Best Practices Guide (F-27360).

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 3211
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of