How are the expansion modules (XP) attached to ACX57xx properly powered when the host ACX is using 12VDC.
  • How are the expansion modules (XP) attached to ACX57xx properly powered when the host ACX is using 12VDC.
  • AbeMeran
    AbeMeran
‎2018-09-11 01:10 PM
Site using 12VDC to power ACX5740s, they need to attach IO expansion modules to the ACX but the XP modules specify they require 24VDC.
ACX5740
ACX5720
XP modules
Documentation
The ACX57xx hardware has been designed to maintain 24VDC on the expansion port over the full 12-28VDC input range of  the ACX, this is accomplished via a boost/buck converter circuit in the hardware.
  • 17405