Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

HotFix Rules

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • HotFix Rules
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Chris_Asbury
    Chris_Asbury
  • sesa139513
    sesa139513
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3600 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

HotFix Rules

Picard Product_Support
‎2018-09-11 07:03 AM

Issue

HotFix best practices

Environment

Site with StruxureWare Building Operation

Cause

Is it supported to have a Hotfix applied to ES/Workstation, but not the AS?
Is it supported to have different HotFixes applied to the same site? In other words, HotFixes can be applied to select AS, but can you have different HotFixes on different AS, with perhaps a different HotFix applied to the ES/WorkStation?
 

Resolution

The hot fix readme details what is necessary to install a Hotfix, generally they can be mixed as necessary on the one site, if there is any dependency’s (i.e. you need to install WS with the ES) this again will be detailed in the HotFix readme file.

Remember HotFixes are now consolidated (all in the one hot fix) and the build numbering of the HotFix shows this, i.e. 1.6.0.xxx is based on fixes consolidated in consolidation point 1, again the readme tells you which fixes are included.

Also remember that you can only apply a hot fix when the build number is greater than the current installed build.
As a general rule you should be able to have different hot fixes on a ES, on an AS and on Workstation. However, installing a new hot fix on top of a previous hot fix for any of these will remove the previous hot fix, if the read me file for the new hotfix doesn't specify that the previous hot fix is included. It will specify this not in terms of hot fix builds but in terms of fixes for ALM defect ID's.

Therefore, one needs to look at the read me files for the combination of hot fixes used at any specific site to make sure all hot fixes needed are effective and not have been overwritten by a later hot fix.

The above is true for read me files whether or not a hot fix is considered to be a consolidated hot fix or not.

Note, the guidelines seem to imply that all hot fixes are consolidated, which is no true.
 

Version of firmware on an AS:

Note: Not all HotFixes apply to all sites. HotFixes eliminate issues observed and defined in a particular defect. 
 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 15807
  • upgrade
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore