Host Trend Log reporting "?" for some values
  • Host Trend Log reporting "?" for some values
  • Tom_Poovey
    Tom_Poovey
‎2018-09-06 03:00 PM
  • I/NET Seven
  • Host Trend Log
The reason for the "?" is because a rule was not complied with. The Print interval/Sample Interval did not result in an even number.
The Basic rule for the "Host Trend Log" is the Print Interval (divided by) Sample Interval – must equal an even number.
For example the default setting in this editor is as follows: Print Interval – 1440 Sample Interval – 30
So 1440/30 = 48
  • TAC INET
  • 2517