Host Lost Message Definition
  • Host Lost Message Definition
  • Derrick_Ratliff
    Derrick_Ratliff
‎2018-09-10 04:51 AM
I/NET
Host Lost messages are caused when I/NET has lost communication over the Ethernet LAN with a host workstation, Xenta 527 or NPR.
Host masks are enabled or disabled by using the far left bit mask of group 1.
You can enable/disable these from showing up in AMT by:
  1. Open AMT
  2. Select Edit>Configuration
  3. Toggle the far left bit of Group 1
  4. Click OK
Alternative Resolution
  1. Open I/NET configuration
  2. Modify the Active Profile
  3. Click Host Masks
  4. Modify Each Host Device
  5. Toggle the far left bit of Group 1
  • TAC INET
  • 6607