Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

History count capacity in Niagara G3 stations and ComTrol CWEB / CES stations

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • History count capacity in Niagara G3 stations and ComTrol CWEB / CES stations
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • sesa116871
    sesa116871

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1371 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

History count capacity in Niagara G3 stations and ComTrol CWEB / CES stations

Picard Product_Support
‎2018-09-06 02:24 PM

Issue

How many histories can be created in a station and how many records are allowed per history?

Environment

I/A Series G3 ENC, ENS or SoftJace
CComTrolCCWEBor CES

Cause

Technical product information update.

Resolution

Regardless of platform type, histories are stored under the station's file system (file:^history/). Stations running on a PC-based system (Enterprise Server or SoftJACE) store the histories in subdirectories using segmented files; this provides improved search capabilities over a flat file system. Stations running on a QNX-based system (ENC) store all of the stations histories in a single compressed file (history.zip). A running station opens the history.zip file in the ENC's ram disk space, the histories are compressed and saved to flash whenever the station is saved. Opening the history.zip file to the ram disk eliminates the need to write to the flash drive each time a record is added to the history file.

 

When the station needs to write a record to a history, it opens the specific history into the running station (either from the file system if PC-based, or from the ram disk if QNX-based). The open history does contribute to the heap.used of the station. The history service has one property 'max open time' (default 5 minutes) which causes the station to close the history from the running station heap if no records have been written to the history for a time period exceeding the 'max open time'.

 

Each history extension which is added to the station does add slightly to the station resources because the extension is represented in the bog file. When the history is first enabled, the station creates the history file. The initial file includes a 1600 byte header (defines the configuration parameters) and a single page file of 4096 byte size. When triggered by either the collection interval or COV/COS, a record is added to the page file. When the page file becomes full, additional page files are created based on the capacity configuration of the history.


History Record Size by Point Type
Point Type bytes/record
boolean 13
enum 16
single precision numeric 16
double precision numeric 20
string variable length *
*NOTE: A single 'string' record cannot exceed one page (4096 bytes)

 

Since histories count as file descriptors, there is a physical limitation on the number of histories allowed in a QNX-based ENC station. It is recommended not to exceed 800 histories, given the file descriptor limit of 1000.
Note: The platform services view of the QNX-based JACE station includes a property to modify the size of the ram disk within defined limitations. Note that the alarm database is also maintained in the same ram disk space. Exercise caution when modifying the default ram disk size; note that allocating additional memory to the ram disk will limit the memory available for other functions by the QNX OS. Reducing the ram disk size too much could result in history or alarm records not being stored properly and erratic station behavior.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 4033
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore