Desire to create a Panel in a subfolder, such as BACnet Application folder.
StruxureWare Building Operation 1.0 and higher
For navigability from the Workstation, it may be desirable to nest a Panel graphic display directly underneath the BACnet controller it is displaying information for.
Panel(s) and inability for creation in the BACnet Application folder is intentional.
The BACnet Application is mostly reserved objects which are visible to BACnet (Points, Values, Alarms, Trends, Schedules, etc), and also non-BACnet objects that you might use with BACnet objects (Graphics, Extended Trend Logs, Charts and Lists). Things that are related to applications.
The Panel object is related to the Workstation and its layout, not the application. Panel objects also cannot be created inside of any other communication protocol interfaces (LonWorks or ModBus, for example).