Graphic fail to load after the Enterprise Server has been running for some time

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Graphic fail to load after the Enterprise Server has been running for some time
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterLarsen
    PeterLarsen

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
194 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Graphic fail to load after the Enterprise Server has been running for some time

Spock PeterLarsen Spock
‎2025-09-07 09:26 PM

on ‎2025-09-07 09:26 PM

Issue

At first, TGML graphics in Building Operation WorkStation load correctly and display real-time values. However, after the Enterprise Server has been running for an extended period, the graphics begin to load slowly, and values stop refreshing or updating.

Restarting the Enterprise Server temporarily restores functionality, but the issue eventually reoccurs.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation WorkStation
  • Building Operation Enterprise Server
  • TGML Graphics
  • SmartConnector

Cause

This issue is typically caused by the behavior of a SmartConnector that:

  • Polls values too frequently
  • Creates a new login session for each poll instead of reusing an existing session

This results in a high number of open sessions with the Enterprise Server. In the SmartConnector view, multiple active sessions can be observed.

The problem tends to occur when there are more than 150 active connections, although this threshold may vary depending on the server’s processing load.

 

image002.png

 

Resolution

To resolve this issue, request the SmartConnector developers to:

  1. Adjust the polling rate to a more appropriate interval
  2. Reuse existing login sessions instead of creating a new one for each poll

These changes will significantly reduce the number of active sessions and improve the performance and reliability of graphic updates in the Enterprise Server.

 

Additional Notes

  • Monitor the number of active sessions via the SmartConnector view.
  • Consider implementing session management best practices to avoid similar issues in future deployments.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • PeterLarsen25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore