Getting "invalid status error 503" when trying to access a Niagara R2 UNC station remotely
  • Getting "invalid status error 503" when trying to access a Niagara R2 UNC station remotely
  • Kim_Baze
    Kim_Baze
  • SESA113595
    SESA113595
‎2018-09-07 01:27 AM
Last Updated: Administrator DavidFisher Administrator ‎2020-10-29 07:27 AM
TAC IA Series
Remote I/A Series R2 station
Issue is due to large number of UNCs on site, and / or high browser traffic.
This is an issue seen from time to time on sites that either have many UNCs present or see lots of browser traffic. Check the system.properties file. There is a line that reads:  webServer.threadPoolSize=15 .
This is the number of web server threads that can be opened to the UNC station.  Each station to station connection takes up one thread, as does a web browser connection.  I believe the JDE takes up three threads when it connects to the UNC station.  If the UNC station runs out of available threads you will see the "503" error. Change that number to 25 or 30 and reboot the UNC. If the problem persists, then change this line to false: ie.activex.activation=true
  • TAC IA Series
  • 3162