Getting an "out of memory error" when converting a station's database from Release 2.301.330 to Release 2.301.529.
  • Getting an "out of memory error" when converting a station's database from Release 2.301.330 to Release 2.301.529.
  • sesa116873_brid
    sesa116873_brid
‎2018-09-06 01:31 PM
Getting an “out of memory error” when converting a station’s database from Release 2.301.330 to Release 2.301.529.
Niagara R2, UNC-520-1, UNC-410-1
The sns file was used to convert database from 330 to 529
The XML copy of a station’s database should be used when bringing older version of R2 databases forward.  Convert the XML file to DB locally. Any errors will be discovered during the conversion.  Fix any error that may appear.
The database can now be downloaded to the UNC