Getting an error when adding the ASD service to a Niagara R2 station
  • Getting an error when adding the ASD service to a Niagara R2 station
‎2018-09-07 02:28 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:42 AM
  • Niagara R2
  • ibsAsd driver
The error indicates that the serialDriver jar file has not been installed.
The ibsAsd driver will not function without the serialDriver jar file. The serialDriver includes communications class files needed to support ibsAsd.
To correct the issue, use the Installation Wizard in the admin tool to install the serialDriver jar.
Caution: The station must have the Serial Driver installed. It is recommended that the 516b version released in July 2006 be used. The jar files as well as the ASD driver documentation (F-27429) are available for download from The Exchange Download Center
  • TAC IA Series
  • 3373