Get "Value does not fall within expected range" error message when trying to view values from a Vista node in webstation.
  • Get "Value does not fall within expected range" error message when trying to view values from a Vista node in webstation.
  • sesa177673
    sesa177673
‎2018-09-10 05:08 AM
  • Vista 5.1.X
  • Webstation 5.1.X
  • Vista in network (master with at least 1 slave)
This is a COM error caused by a difference in regional settings on the Vista servers. E.g. 100 000.00 may be retrieved as 100,000.00 if other settings are used on another server. This will cause a mismatch.
Ensure that the settings for digit grouping and decimal symbol are the same on all Vista servers.
  1. Click on Start\Control Panel\Regional and language options.
  2. Select Customize and check the settings on the Numbers tab.
  3. Compare these settings with the other Vista servers.
  • 6879