Get "Invalid System Enumeration" error when polling an XDriver point
  • Get "Invalid System Enumeration" error when polling an XDriver point
  • YangboLIU
    YangboLIU
‎2018-09-06 09:50 AM
After configuring an XDriver point, clicking the refresh button on the editor results in an error "Invalid system enumeration" and no value response from the Slave device.
  • BCX1
  • Cyberstation 1.9X
  • Modbus RTU
There is a register number shift (+1 or -1) some equipment uses. The registers listed in the manual do not actually exist.
Add a register number shift (+1 or -1) to the register number listed in the manual.
  • 15109