Get "Error: Device type specified in MTA file is not what TAC Vista expected, Info: Download Application and Parameters" when downloading to a Xenta controller from TAC V...
  • Get "Error: Device type specified in MTA file is not what TAC Vista expected, Info: Download Application and Parameters" when...
  • sesa150555
    sesa150555
‎2018-09-06 01:53 PM
Get "Error: Device type specified in MTA file is not what TAC Vista expected, Info: Download Application and Parameters"  when downloading to a Xenta controller from TAC Vista.
TAC Vista
TAC Xenta 30x, 28x, 401
The type of controller that you specify in the device specification in the Menta application have the be to exact type you are downloading to.
So either there is a mismatch or there is another controller on the network with the address you are using.
  1. Right click and Edit the controller in TAC Vista Workstation.
  2. Log in to view the Menta application
  3. Check in Options > Device Specification that it is the right type.
  4. If not, change to the right type.