Generating an XIF in XBuilder for a Xenta 5/7/9xx device. Where is the XIF file located?
  • Generating an XIF in XBuilder for a Xenta 5/7/9xx device. Where is the XIF file located?
  • sesa150555
    sesa150555
‎2018-09-06 03:05 PM
XBuilder
If you right click on the root object of the network pane of XBuilder (on the Xenta 5/7/9xx object) and choose "Generate XIF File," a window pops up that says "XIF File generated."  But it doesn't tell you where it put it.
  1. Find the XIF in \\your project\Target image\configdb\lon.
  2. The file is named TAC_XENTA_527.xif (for example)
  3. Check the time stamp on the file to double check that it is the correct one that was just generated.
  • 2028