Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

G3 schedules stop working after Daylight Savings Time (DST) changeover

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • G3 schedules stop working after Daylight Savings Time (DST) changeover
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1217 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

G3 schedules stop working after Daylight Savings Time (DST) changeover

Picard Product_Support
‎2018-09-07 06:34 AM

Last Updated: Crewman ContentModerator ‎2025-10-15 03:38 AM

Issue

Some schedules stop operating correctly after Daylight Savings Time (DST) changeover. 

Environment

I/A Series G3, all ENS and ENC with builds 3.5.4, 3.4.53.1, 3.3.31.2, 3.2.23.1 or earlier.

Cause

Any station with a schedule, of any type, with an event set to occur during the "advanced" (missing) hour between 2:00 AM and 3:00 AM on the DST changeover day. The resulting miscalculation of the schedule's "Next Time" or "Next Trigger" time could cause that schedule, or even other schedules in the station, to stop working.

This typically affects downstream logic in the station. In some cases it was observed that the CPU usage on an ENC went up to 100% while calculating invalid next event times.

Examples

  • A station contains a BooleanSchedule with events at 12:00 AM and then again at 2:05 AM daily. At 12 AM the schedule executes normally and attempts to calculate the next event time. On the second Sunday in March the next event time calculates to a time that does not exist due to the DST change. This causes the Java thread that executes all schedules in the station to become tied up attempting to recalculate the time.
  • A station contains a TriggerSchedule that periodically repeats every 15 minutes, with a range passing through the DST changeover time. On the second Sunday in March the next trigger time calculates to a time that does not exist (say, 2:15 AM). Again, this causes the Java thread that executes all schedules to become tied up attempting to recalculate.

Resolution

The solution to this issue is to upgrade the schedule.jar file in the platform to one of the versions below, or later. Files are available from The Exchange Extranet. 

  • Release 3.3.31.2 (Download and extract schedule-3.3.34.1)

If you are using a build that is higher than the above versions then you will not be affected by this issue.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 4593
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore