G3 ASD (tacAsd) driver setup basics.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • G3 ASD (tacAsd) driver setup basics.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • WaynePeters
    WaynePeters
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1698 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

G3 ASD (tacAsd) driver setup basics.

Picard Product_Support
‎2018-09-06 02:00 PM

Issue

Provides additional setup information for the G3 ASD (tacAsd) driver implementation.

Environment

G3 ASD (tacAsd) driver (all revisions)

Cause

None

Resolution

G3 ASD (tacAsd) driver setup basics ...
 

Monitor properties

Ping Enabled = true
Ping Frequency = 5m change to 1m
Alarm On Failure = true
Startup Alarm Delay = 5m

The baud rate sync properties is the mechanism that synchronizes the baud rates for the ASD bus. Upon reset, ASD devices initialize to 1200 baud and it is this mechanism that locates those devices and sets the baud rate to 19.2K or 9.6K (if PEMs are used on the bus). These values are part of the ASD specification and should not be changed.

Last Time Sync is the last time a successful sync occurred
Baud Rate Sync Time = 1m
Baud Rate Set Timeout = 0.2s
Baud Rate Set Repeat = 1
Baud Rate Change Millis = 800

Total Devices indicates the total number of devices active.
Total Down indicates the total number of down devices.

Scan Time indicates the total time to poll through the list if devices. The ASD communications protocol is designed to exchange most data between the host (ENC) and device with one transaction. This means that typical data (e.g. EMS, etc.) is written to the device as part of the request and response data (e.g. Window, Output, Diagnostics, etc.) in one transaction. In this case, the scan time is 6.9 seconds for 33 devices or approximately 4.5 devices per second.

Tuning Policies (Default Policy)

Min Write Time = 0
Max Write Time = 0
Write On Start = false
Write On Up = false
Write On Enabled = false
Stale Time = 0

Note: The stale time actually involves the proxy point objects. The polling mechanism still continues and the internal point information is still updated. The driver does not implement the interaction between the point updates and proxy point stale. The values should be left at their default settings.

Poll Scheduler

Poll Enabled = true

Fast Rate = 5s (defaults to 1s)
Normal Rate = 10s (defaults to 5s)
Slow Rate = 30s (defaults to 30s)

Typically set the Normal Rate based upon the rules specified in the R2 documentation or (Normal Rate seconds = Number of devices / 3.5). For example, a network with 33 devices would be set to (33 / 3.5 = 10 seconds). As indicated earlier, the driver inherits the basic driver properties and mechanisms. G3 implements a complex poll scheduling mechanism that automatically determines and continually adjusts the poll list to achieve the most efficient polling.

Retry Count

The retry is only used in the event that a response from an ASD device is not received.  This value defaults to 1 and can be increased if needed to a maximum of 3 if devices are unable to respond to the initial message and one subsequent retry,  Devices that do not respond to the initial message may indicate a potential issue with the ASD bus.

Response Timeout

This is the amount of time the driver will wait for a response to a request before retrying the request.  This value defaults to 2 seconds and should not be changed.

Inter Message Delay

This value defaults to 0 seconds and should not be changed.

Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 4820
  • minimum
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of