Functional block names are shorter in XIF file, LonMaker or NL220 than the names defined in SmartStruxure

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Functional block names are shorter in XIF file, LonMaker or NL220 than the names defined in SmartStruxure
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
6949 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Functional block names are shorter in XIF file, LonMaker or NL220 than the names defined in SmartStruxure

Picard Product_Support
‎2018-09-11 07:46 AM

Last Updated: Crewman ContentModerator ‎2025-10-10 02:55 AM

Issue

Functional block names are shorter in XIF file, LonMaker or NL220 than the names defined in SmartStruxure

Environment

Automation Server

Externally Managed LonWorks Network

Cause

LonMark defines how a xif file must be structured and written. There are especially three rules that comes into play when creating the functional blocks from an Automation Server in the externally managed LonWorks network.

In the LONMARK® Device Interface File Reference Guide it states that: "If the static interface contains functional blocks, the device selfdocumentation string must be formatted as described in The LONMARK Interoperability Guidelines."

In the LONMARK® Application-Layer Interoperability Guidelines it states that: "Manufacturers are free to assign any functional profile number to new non-inheriting profiles, as long as they are in the range of 20000 to 25000, inclusive; and as long as the number is unique for the program ID template and scope of the resource file set containing the functional profile."

In the same document it also states that: "The device self-documentation string is a string of up to 1024 bytes (subject to device memory limits)" and also "If the name is text, it must consist of ASCII printable characters, be of no more than 16 characters in length".

Due to the above mentioned rules, any functional block defined in the Automation Server will always start with a functional profile number from 20001 and up and the name of the functional block (excluding the 5 digit profile number) will not be longer than 16 characters. If the name defined in SmartStruxure is longer than 16 characters, the characters from 17 and up will be deleted. If the complete length of the self documentation string is longer than 1024 bytes, the maximum character length will be lowered by one until the complete string fits within 1024 bytes.

Resolution

The only way to get around this is to either make fewer functional blocks on the Local Node in SmartStruxure, or to make their names shorter.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
Tags (2)
  • Find more articles tagged with:
  • 16678
  • PeterLarsen25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore