Function Block Program fails to deploy

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Function Block Program fails to deploy
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1605 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Function Block Program fails to deploy

Guinan RobertAndriolo Guinan
‎2024-10-31 06:54 PM

Issue

When attempting to save & deploy a function block program using Modernized Programming, the following errors are seen:

EBO 2022 - Deploy program error: The program was not deployed! (Error Code - 1073740940)

FBP-DeployErrorEBO2022.png

EBO 2024 - Deploy program error - Invalid data "Empty binary file' Invalid data 

FBP-DeployErrorEBO2024.png

Product Line

EcoStruxure Building Operation

Environment

  • EcoStruxure Building Operation WorkStation EBO 2022
  • EcoStruxure Building Operation WorkStation EBO 2024 
  • Function Block Programs (Builder for Function Block)

Cause

Related to known issue Modernized Programming Builder program error during deploy

This is when the TEMP / TMP User variable folder paths contain a space; this can be edited in the Environmental Variables. 

Resolution

Edit the TEMP and/or TMP paths so that they do not contain any spaces. 

To edit the Environmental Variables, follow these steps: 

  1. 1. Click on the Start Menu button located at the bottom-left corner of your screen.
  2. In the search bar, type "environment variables" and press Enter. 
  3. Click on the "Edit the system environment variables" option from the search results. This action will open the System Properties window, which contains various tabs and settings for your computer.
  4. In the System Properties window, click the "Environment Variables" button located at the bottom right. Clicking this button will open another window specifically for managing environment variables. 
  5. In the Environment Variables window, under the "User variables" section, "Edit" the path that contains any "spaces".  These paths can be located anywhere on this PC. 
    EnvironmentVariables-User.png
    User variables apply only to your account, while system variables affect all users on the computer. Choose accordingly, and then add or edit variables as needed.
  6. Once you have completed these steps, your new or edited environment variables will take effect. 
  7. Restart WorkStation, and the program should now deploy successfully. 

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • RobertAndriolo24
Was this article helpful? Yes No
67% helpful (2/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.