Forta actuator only modulates 0-50% when given a 0-10V input signal
  • Forta actuator only modulates 0-50% when given a 0-10V input signal
‎2018-09-11 01:13 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:42 AM
Forta actuator only modulates 0-50% when given a 0-10V input signal.  All DIP switches are OFF, so it should modulate 0-100% for 0-10V input.
Forta
M800
If the X1 and MX control signal connections are reversed, the actuator will appear to modulate but the stroke will be limited to 0-50%
Ensure that the actuator is correctly wired, according to the Forta datasheet.