Issue
For a high temperature application, how can a TS-8204 be programmed to read accurately when connected to a MNL controller?
Environment
TS-8204
Cause
Require instruction on configuring the TS-8204 temperature sensor for accurate reading.
Resolution
Connect the TS-8204 sensor and install a 2.49 kohm resistor in parallel (1% resistor or better).
Set the Analog Input object to Balco and link the output to a Curve Fit object.
Curve Fit objects are supported only on controllers with Rev.3. They are not supported on VAV controllers.
Configure the Curve Fit X and Y data points as follows:
- Data Point X1 10.8
- Data Point X2 34.5
- Data Point X3 57.0
- Data Point X4 78.0
- Data Point X5 97.8
- Data Point X6 116.4
- Data Point Y1 200
- Data Point Y2 240
- Data Point Y3 280
- Data Point Y4 320
- Data Point Y5 360
- Data Point Y6 400