The Workplace Tech Tool 4.0 Engineering Guide (F-27254), Chapter 3 - "S-Link Sensor Tags", states "PBOccMode" is 0 following a download or reset.  This is incorrect.  Following a download or reset, the PBOccMode tag comes back as NA.
Lon and BACnet controllers with MN stats
error in documentation
There is a work around if a 0 is required following a download or reset. If the existing logic is not able to handle the "NA", then link PBOccMode into Input[1] of a two input "Priority Object". Set Input[2] to a constant of 0. The Priority object will output a 0 following a download or reset.