Filter an alarm listview by EventNotification
  • Filter an alarm listview by EventNotification
  • ScottLeedberg
    ScottLeedberg
‎2018-09-06 02:39 PM
Alarm Listview
The way to do this is to create a listview of class AlarmEvents and put the columns you want displayed on the columns tab.
  1. To set up the filtering go to the Qualifiers Tab and under the database section select the checkbox "Advanced Database Qualifier".
  2. In the qualifier box you will need to type in the statement below
    EventNotificationClassID is like (put full path and name of the EventNotification here) id
  3. You need to manually type the above in the qualifier box because if you use the wizard the attribute is not listed correctly.