File Master appears to work with the Equalized Client, but will not replicate

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • File Master appears to work with the Equalized Client, but will not replicate
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Tom_Poovey
    Tom_Poovey
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1227 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

File Master appears to work with the Equalized Client, but will not replicate

Picard Product_Support
‎2018-09-06 01:57 PM

Issue

Filemaster is Full SQL 2005 and Equalized Client is SQL Express fails to equalize. 

Environment

  • Full SQL 2005 for the Filemaster
  • SQL Express for the Equalized Client
  • 2.31 version of TAC I/NET Seven
  • 2.4x version of TAC I/NET Seven

Cause

 SQL Express doesn't start equalization services automatically.

Resolution

The Equalized Client refused to replicate the database with the Filemaster. Equalization is not succeeding even though the little icon may say it is equalized. Filemaster shows pending. Start I/NET and check the host passwords to see if equalization has taken place.

  1. The following steps will cause equalization to take place: 
  2. Restart the pc to ensure there isn't a program hanging in the memory.
  3. Demote Equalized Client to Stand Alone.
  4. Exit I/NET and I/O Server
  5. Go to Start/Run/CMD
  6. Maneuver to the C:\Program Files\Inet Seven folder and type the following: 
  7. ineteqzmerge /unregserver     press the Enter key
  8. ineteqzmerge /service     press the Enter key
  9. Now go to Services by selecting My Computer/Manage/Services and look for the Service running called InetEQZMerge and start the service and select Automatic.
  10. Now you should promote the I/NET workstation to Equalized Client ensuring you put the Filemaster Name rather than IP address.
  11. The snapshot will be delivered to the Equalized Client. After equalization you may need to shut down I/Net and the I/O Server one last time and then restart I/NET Seven.
  12. Now return to Services by selecting My Computer/Manage/Services and look for the Service running called InetEQZMerge where you should STOP then START the service again. 

One way to test equalization from Filemaster to Equalized Client: in I/NET Seven under Edit/Host Computer/Passwords add a user/password. Check the other computer to see if the database replicated the new user/password and Vice Versa.

If ineteqzmerge is already running as a service.  Try stopping and starting the service.

Labels (1)
Labels:
  • TAC INET
Tags (2)
  • Find more articles tagged with:
  • 4932
  • replicateing
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore