Field Devices - Replacement for a V295 steam valve and an M750 actuator.
  • Field Devices - Replacement for a V295 steam valve and an M750 actuator.
‎2018-09-06 12:49 PM
Last Updated: Crewman ContentModerator ‎2025-08-11 04:01 AM
V295
Steam Valve
M750
Actuator
Unable to purchase a V295 steam valve and an M750 actuator.
The V295 steam valve and an M750 actuator are obsolete.
M750 - 24v - 880-0010-000 -  Not available -
To operate on steam you will require a spring return actuator, the M700-SRSU (880-0430-000).
V295 - DN 40, PN25, KVS25 - Not available.
A replacement could be the VGS211F-40CS please note this valve has a rating of PN16, where as the V295 was PN25.
To review the VGS211F data sheet, please click HERE.
To review the M700 data sheet, please click HERE.