Issue
Replacement for a V295 steam valve and an M750 actuator.
Environment
V295
Steam Valve
M750
Actuator
Cause
Unable to purchase a V295 steam valve and an M750 actuator.
Resolution
The V295 steam valve and an M750 actuator are obsolete.
M750 - 24v - 880-0010-000 - Not available -
To operate on steam you will require a spring return actuator, the M700-SRSU (880-0430-000).
V295 - DN 40, PN25, KVS25 - Not available.
A replacement could be the VGS211F-40CS please note this valve has a rating of PN16, where as the V295 was PN25.
To review the VGS211F data sheet, please click HERE.
To review the M700 data sheet, please click HERE.