Fiber Optic Interface alternative from Westermo

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Fiber Optic Interface alternative from Westermo
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa139513
    sesa139513
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2112 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Fiber Optic Interface alternative from Westermo

Picard Product_Support
‎2018-09-06 11:50 AM

Issue

Alternatives to the FOI1 and FOI2 product which is discontinued and possible replacement using the Westermo ODW-730-F2

Environment

Site using a Fiber Optic Interface on LAN (CLAN) or SCU Network (SubLAN)

Cause

Discontinuation of the FOI1 and FOI2 products which have been available for a number of years.

Resolution

The ODW appears to provide a very cost effective and versatile fiber optic interface for RS485 networks. The ODW is one of only a few RS485/Fiber interfaces that provide the redundant fiber network capability.
Some notable features on the ODW-730-F2 include –
-Dual Fiber Bus Configuration or Dual Fiber Redundant Ring Configuration
-Local status contact output indicates fiber fault detection
-LED indication of Local fiber fault condition (FL L)
CH1 and CH2 LEDs indicate if failure is on incoming or outgoing fiber
-LED indication of Remote fiber fault condition (FL R)
Here the LED indicates when there a fault anywhere in the system.
A summary of controller status points monitoring the Local fault detection would be reviewed to identify location of a fault. Current system operation is probably operating on the basis of the redundant ring. A second fiber fault will disable the ring system. In a bus configuration, you currently have lost some portion of the system communications.
-Supports Asynchronous (SubLAN) and Synchronous (CLAN) protocols
In the case of the synchronous CLAN interface, it is not reconstructing RS485 data quality. Any accumulated distortion on the copper cable segment is passed on to the data through the fiber and will arrive at the other fiber drops in the same condition, although amplitude will be replenished. You must insure you do not exceed copper cable distances and maintain compliance with recommended grade of cable while avoiding stubs and the distortion they produce.
-Alternate Fiber Interface Options are supported two receptacles for plug-in fiber transceiver module purchased separately
The lowest cost and most common interface is the MLC2. Each of the ODWs in this evaluation were configured with 2 of the MLC2 modules
- MLC2 Multimode 62.5/125um or 50/125um 2km Fiber Length
- SLC20 Singlemode 9/125um 20km Fiber Length
- SLC120 Singlemode 9/125um 120km Fiber Length
The ODW also supports the option of bidirectional fiber interface modules. These are more expensive options and currently used infrequently and are not discussed/evaluated here.
-Powered by 24VAC (48-62hz), or 12 to 48VDC (supporting redundant DC)
Power input is isolated from RS485 and Status port signals
-RS485 port is isolated from power AND local ground
The RS485 will take on the ground reference of the incoming RS485 signals. An oscilloscope examination of the RS485 data pins with no connection to other RS485 devices will show AC voltage on the RS485 pins (leakage to isolated circuit). A scope should only be examined with the RS485 port connected to the CLAN or SubLAN.

Please find the attached pdf ODW FOI EVAL 120824.pdf for review. It proceeds through a sequence of differing configurations with the synchronous controller LAN and the asynchronous SubLAN.

Labels (1)
Labels:
  • TAC INET
Attachments
Tags (1)
  • Find more articles tagged with:
  • 11144
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore