External binding to temperature input shows incorrect value

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • External binding to temperature input shows incorrect value
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • PeterEdvik
    PeterEdvik

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3526 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

External binding to temperature input shows incorrect value

Janeway PeterEdvik Janeway
‎2019-05-22 12:46 AM

Issue

A temperature input on one device is referenced in an external binding, e.g. a consumer value, in another (BACnet) device. The value on the consumer side is incorrect and seems to have been converted from Fahrenheit to Celsius although the units all show Fahrenheit.

External_binding_Incorrect_value.png

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Workstation
  • Building Operation Automation Server (Premium)
  • Building Operation Enterprise Server / Enterprise Central
  • BACnet Device(s) supporting external binding (e.g. MP-X or IP-IO)

Cause

The probable cause is that the value of the temperature input is not configured to a specific unit. This means that the unit is decided by the electrical type of the thermistor. In most cases this is Temperature °C, which means that the values are stored in °C, and this is the value being transferred in the consumer binding.

If the measurement system in Workstation is set to United States Customary Units (US), the input value will be displayed in Fahrenheit (°F) and one might think that the unit of the temperature input value is also configured to Fahrenheit, when in reality it is in Celsius.

In this situation the value on the consumer side is in Celsius as it has no information about units. Furthermore, if the consumer value unit is configured to Fahrenheit, then we have the situation shown in the screenshot above.

Resolution

  1. Start by changing measurement system in Workstation to As configured in object. (Refer to the Webhelp for more information about how to do this.) By doing this the values will be displayed unconverted.

    External_binding_As_configured_in_object.png

    It is now clear that the temperature input in reality is in Celsius.

  2. The next step is to configure the input unit to Fahrenheit. Open up Properties for the Temperature input and click the gear wheel next to Value to configure.

    Value_Configure.png

  3. Check the box to the left of Unit and click the button with the three dots to the right.

    Configure_unit.png

  4. Select °F and click Select

    SelectFarenheit.png

  5. Click OK to confirm the changes in both open windows.

Both the temperature input and the consumer value will now be displaying the correct value in Fahrenheit.

Correct_Values.png

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • PeterEdvik19
Was this article helpful? Yes No
75% helpful (3/4)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of