Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Extended trend log (ETL) does not fill to capacity

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Extended trend log (ETL) does not fill to capacity
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • AbeMeran
    AbeMeran

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1801 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Extended trend log (ETL) does not fill to capacity

Captain AbeMeran Captain
‎2021-07-21 05:27 PM

Last Updated: Picard RobertAndriolo Picard ‎2023-02-13 12:44 PM

Issue

The extended trend log contains approximately 50% of the configured storage capacity.

For example, only 250 entries are in the Trend log view even though the ETL is configured for 500 entries.

2021-07-12_11-36-39.jpg

 

After the ETL runs long enough to fill up the 500 entry capacity, ONLY 250 entries are shown in a Trend log list view. (see below)

 

2021-07-12_11-32-02.jpg

Product Line

EcoStruxure Building Operation

Environment

Building Operation Enterprise Server

Cause

An extended trend log (ETL) includes an equal number of internal entries hidden from view; these entries are overhead incurred in the operation of the ETL. For example, each time a transfer takes place, an internal entry is added.

Depending on the specifics of the configuration (i.e., Maximum Transfer Interval), the percentage of internal entries for a given ETL relative to its full size varies.

From EBO 3.2.3, the internal entries of an ETL are hidden, and no information is provided to give any visibility into how much storage is being used by internal entries.

Resolution

The solution is to increase the size of the ETL to ensure there is enough storage capacity for data and overhead.

Typically, the size must be doubled (in this case, 1000) in the particular ETL to make sure 500 entries of data can be stored. 

Although these transfer events are hidden, it is possible to identify these events by adding the Sequence number column in the trend log list.  It is also possible to decrease the overhead amount stored in the ETL by increasing the "Maximum transfer interval" in the ETL properties, as shown in the screenshots. 

Here it can be seen that by increasing the Maximum transfer interval to 1 hour for an interval log of 5 minutes that ONLY 1 'overhead' record (sequence # 565) is added per 10 entries.  

ETL-SeqNum.png

Using this or a similar setting will allow to reduce the storage requirement of the ETL.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (10)
  • Find more articles tagged with:
  • AbeMeran21
  • entries
  • etl
  • extended
  • internal
  • log
  • overhead
  • RobertAndriolo23
  • size
  • trend
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore