Excessive alarms coming into Vista Workstation from change of state objects
  • Excessive alarms coming into Vista Workstation from change of state objects
  • Derrick_Ratliff
    Derrick_Ratliff
‎2018-09-06 02:06 PM
Vista
Alarm parameters may be set to be too sensitive for the hardware they are monitoring.
Change of State Parameters:
  1. Right Click on the Change of State Object
  2. Select Properties
  3. Click on the Alarms Tab
  4. Change the High and Low Alarm limits to decrease potential alarms
  5. Increase the minimum change to increase the deviation required for an alarm to trip.