Excessive I/A Series G3 NiagaraNetwork worker creation triggers high CPU usage and/or OutOfMemoryError

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Excessive I/A Series G3 NiagaraNetwork worker creation triggers high CPU usage and/or OutOfMemoryError
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • WaynePeters
    WaynePeters
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1848 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Excessive I/A Series G3 NiagaraNetwork worker creation triggers high CPU usage and/or OutOfMemoryError

Picard Product_Support
‎2018-09-07 08:47 AM

Issue

After upgrading systems to the latest I/A Series G3 Niagara maintenance builds 3.5.406, 3.6.406 or 3.7.106 some customers have noticed spikes in Heap and CPU usage. This behavior has been traced to the excessive creation of NiagaraNetwork worker threads.

Customers may see spikes in CPU usage that randomly occur and persist until system appears to halt or in some cases triggers Engine Watchdog Timeout and restart of station.  Customers may also experience the Java Virtual Machine exit with the following exception in the standard output:

java.lang.OutOfMemoryError: unable to create new native thread

Environment

I/A Series G3 versions 3.5.406, 3.6.406, and 3.7.106

Cause

It is believed that excessive NiagaraNetwork workers are being spawned due to additional overhead required to encrypt and decrypt passwords from the new password store utilized in 3.5.406, 3.6.406 and 3.7.106.

Excessive usage of CPU and creation of worker threads may be seen on both Enterprise Network Server and ENC/JACE platforms. Typically OutOfMemoryError will be seen on ENC/JACE platforms and not on PC based solutions due to the limited resources of the embedded platforms.

The issue has only been observed on stations with five or more station devices in the NiagaraNetwork.

Resolution

Limit the number of NiagaraNetwork/workers that can be created by setting the property "Max Threads" on the NiagaraNetwork/workers property sheet.

A good rule of thumb for the number of workers is six times the number of Niagara Network stations monitored by the station.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 14612
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore