Every b3 wireless controller can be brought online, but no two wireless controllers can be online at the same time
  • Every b3 wireless controller can be brought online, but no two wireless controllers can be online at the same time
  • YangboLIU
    YangboLIU
‎2018-09-06 10:19 AM
Every b3 wireless controller can communicate with BCX1 separately, but when there is a b3 wireless controller is online, the other controller can't be brought  online, the online controller must be powered off or remove the adapter, otherwise, the others will never be online.
Continuum Cyberstation
BCX1 wireless
B3 wireless
If the wireless adapter and wired RS485 was connected, this issue will happen.
  1. Remove the wired RS485 connector from the controller or disconnect the MS/TP bus,
  2. From the Comm2 port of BCX1, click "learn", All the b3 wireless controller will come online quickly
Tags (2)
  • 13540
  • offline